What is the fuse size required for the 50 kVA transformer bank?

Prepare for the 4th Year Lineman Apprentice Exam. Study with interactive resources including flashcards and multiple choice questions, each offering hints and explanations. Get exam-ready today!

To determine the appropriate fuse size for a 50 kVA transformer bank, it's essential to first calculate the full-load current based on the transformer's rating. The full-load current can be calculated using the formula:

Full Load Current (Amps) = kVA × 1000 / (Voltage × √3) for three-phase transformers, or

Full Load Current (Amps) = kVA × 1000 / Voltage for single-phase transformers.

Considering a three-phase transformer as is common in many applications, and using a standard voltage level of 480 volts for calculation, the full-load current would be calculated as follows:

Full Load Current = 50 kVA × 1000 / (480V × √3) ≈ 60.2 amps.

The fuse sizing for transformers typically also considers a fuse rating that is sufficiently above the full-load current but within safe limits to protect the transformer from damage due to overload or faults. A common practice is to size fuses at 125% of the transformer’s full-load current for primary fusing.

Taking the calculated full-load current of approximately 60 amps, 125% would yield about 75 amps as a recommended fuse size to provide adequate protection to the transformer while allowing for some